Hi @kostek184-coder, Short answer: zero sequence parameters of a transformer are dependent on the winding types at both sides. For example:
Hope this helps! If you;d like our documentation to be more detailed, feel free to make an issue ;) |
Beta Was this translation helpful? Give feedback.
-
|
To start with positive and negative sequence admittance is modelled from the transformer rating in a pi model with each leg equal. Simply put, zero sequence parameters are modelled equally as positive sequence parameters in transformers in pi model with extra conditions as follows:
Nomenclature
Symmetric modelling for any branch in PGMConnected branchespi-model for all branches in PGM From side disconnectedTo side disconnectedAsymmetric Modelling for TransformersPositive sequenceSame as symmetrical modelling with following: Negative sequenceSame as symmetrical modelling with following: Zero SequenceZero sequence admittances for a transformer depends on the winding configuration. YNynSame as symmetrical modelling with following: YNd
Dyn
ZN*
*zn
All other winding configurationsPhase wise admittancesEventually these sequences admittances are converted into three phase values (012 -> abc) as PGM's solver operates on the phase domain. |
Beta Was this translation helpful? Give feedback.

Uh oh!
There was an error while loading. Please reload this page.
-
How is a transformer modeled for zero sequence? There's no way to specify R0 and X0 as for a line.